Posted:
Sat Apr 12, 2008 9:09 am Post subject:
Parks with Electrical Problems |
|
|
Because of my inverter sensitivity, I have begun to notice which parks have electrical problems. I have noticed open ground or Neutrals, fluctuating voltages, etc. With an open ground, I have detected up to10 volts potential from the skin of my coach to earth - enough to knock you on your butt.
I think it is time to name names and let's force these people to bring their electrical systems up to code!
San Augustine Corp of Engineers park on the Sam Rayburn Reservoir in Texas: open ground.
Coachlight RV Park, Carthage, MO: Open ground or Neutral
I would appreciate input from others on parks they have found with electrical problems. _________________ SHvnDave
SHvnJudy
& Buffy
Living in a 99 Monaco Diplomat |
|
| Back to top |
|
 |
elh3946

Joined: 06 Nov 2005
Posts: 1650
Location: Sioux Falls, SD
|
Posted:
Sat Apr 12, 2008 11:56 am Post subject:
|
|
|
| I hope you are notifying the RV parks of the problems; otherwise, they may not be aware of them and, thus, can't do anything to correct them. |
|
| Back to top |
|
 |
SHvnDave
Joined: 20 Jan 2007
Posts: 22
Location: Livin at our License Plate
|
Posted:
Sat Apr 12, 2008 9:41 pm Post subject:
Park Electrical |
|
|
I have, of course. One park acknowledged the problem and the other, even when presented with the meter readings, denied any problems. I have also spent $100 to ensure that my electrical system is properly functioning - it is - and I have no problems with most parks. But now when I hook up, I test first - it is that important. _________________ SHvnDave
SHvnJudy
& Buffy
Living in a 99 Monaco Diplomat |
|
| Back to top |
|
 |
jrf
Joined: 20 Jul 2006
Posts: 250
|
Posted:
Sun Apr 13, 2008 6:13 am Post subject:
|
|
|
but now when I hook up, I test first - it is that important.
---
Plenty of RV parks, especially older places, have incorrectly-wired pedestals; this is hardly a "new" problem. But yes, it is that important to test the quality of the power coming out of the pedestal before hooking up. But I stopped being surprised a long time ago at how many people just plug in with no thoughts as to the safety or adequacy of the power supply.
Folks might want to look at www.surgeguard.com or www.progressiveindustries.net and invest in a good power line monitor, either portable or hard-wired. I've heard plenty of people say that a power line monitor is "too expensive"; I wonder if they've looked at the cost of re-wiring their rig? [/b] |
|
| Back to top |
|
 |
SHvnDave
Joined: 20 Jan 2007
Posts: 22
Location: Livin at our License Plate
|
Posted:
Sun Apr 13, 2008 4:08 pm Post subject:
|
|
|
I agree that a surge protector/circuit tester is an excellent idea and everyone should invest in one; however, I also would like to start holding the park owners feet to the fire by posting the names of the parks where the power system is either potentially damaging to the coach or possibly dangerous to the occupants. As I said, getting 10V AC with your feet wet will give you a whole new outlook on this problem. _________________ SHvnDave
SHvnJudy
& Buffy
Living in a 99 Monaco Diplomat |
|
| Back to top |
|
 |
Adrienne
Site Admin

Joined: 03 Nov 2005
Posts: 747
Location: Cyberspace and anyplace
|
Posted:
Sun Apr 13, 2008 4:26 pm Post subject:
|
|
|
I would caution you to send an email or certified postal letter to the parks informing them that if they do not respond or immediately comply with safe electrical operations, the names and locations of their parks will be made public. In today's litigious society, you could be sued if, in the interim between your letter and your post, they have repaired or upgreaded their system to code.
Once you have published their names, it's very difficult to repair their reputation. The damage will already have been done.
I'm not an attorney by any means but I advise you to wait before publishing any more names. Thank you. _________________ Best--
Adrienne Kristine
Forum Administrator
http://www.RVTravel.com
http://www.FreeCampgrounds.com
http://twitter.com/AdrienneAXK |
|
| Back to top |
|
 |
tantamount

Joined: 15 Apr 2007
Posts: 211
Location: roaming
|
Posted:
Sun Apr 13, 2008 9:42 pm Post subject:
Re: |
|
|
| jrf wrote: | I've heard plenty of people say that a power line monitor is "too expensive"; I wonder if they've looked at the cost of re-wiring their rig? [/b] |
And I wonder how many CG owners have looked at THEIR cost of rewiring my rig? I'm not a litigious person by nature and I have and use the capability to monitor my electrical system, but it is NOT my responsibility to do so. There is a plethora of precedent to establish culpability on the part of the provider in cases like these. |
|
| Back to top |
|
 |
Alterego

Joined: 12 Jan 2006
Posts: 596
|
Posted:
Mon Apr 14, 2008 7:52 am Post subject:
|
|
|
| Every electrical system in any park (Fed, State, County, City, or Private) is covered under the NEC (National Electric Code). If you find a problem and management refuses to repair it, NOTIFY the Electrical Inspector who has jurisdiction over that particular area. {Most normally it will be the local County Electrical Inspector that you would need to notify.} It is the electrical inspector's job to order repairs be made to be in compliance with code, and power be shut off if safety is an issue. |
|
| Back to top |
|
 |
tantamount

Joined: 15 Apr 2007
Posts: 211
Location: roaming
|
Posted:
Mon Apr 14, 2008 10:28 am Post subject:
Re: |
|
|
| Alterego wrote: | | Every electrical system in any park (Fed, State, County, City, or Private) is covered under the NEC (National Electric Code). If you find a problem |
I just want to emphasize my point. It is NOT the responsibility of the camper/consumer to "find" a problem. Is it wise, prudent and to the advantage of the user? Of course, but it is not required in a liability situation. |
|
| Back to top |
|
 |
jrf
Joined: 20 Jul 2006
Posts: 250
|
Posted:
Mon Apr 14, 2008 11:17 am Post subject:
|
|
|
There is a plethora of precedent to establish culpability on the part of the provider in cases like these.
---
Perhaps so, but in real life, the burden of proof is still on the person whose rig's sytem was damaged. Since the process of establishing responsibility and collecting damages would very likely involve lawyers, insurance companies, and possible court proceedings, I suspect that it would be a very long, complex, and expensive procedure! And I would bet that the guy with the fried wires would be the one to suffer the greater inconvenience, hassle, and expense trying to prove an RV park's liability. YMMV. |
|
| Back to top |
|
 |
SHvnDave
Joined: 20 Jan 2007
Posts: 22
Location: Livin at our License Plate
|
Posted:
Sat Sep 27, 2008 6:18 am Post subject:
My Solution |
|
|
Since I first posted here, I have invested in a surge guard to monitor and protect my system (trips at >134V or <92V).
I am also building a box that will be mounted on a grounding rod. The box will plug into a 30A outlet and my 50A plug will plug into the box. The ground rod will be connected to the neutral connection and driven a foot into the earth to ensure I see zero volts on my neutral.
If the ground is not at zero volts, I will connect a separate line at my rig to go directly to earth - this keeps the neutral and the ground several feet apart and should solve most problems.
Note that when you have traveled 8-10 hours and pull into the only campground around, it doesn't matter whether the problem is the campground's because the problem WILL BE yours.
Adrienne - I would really like to see an article in RV Travel so more RVers and park owners become aware of the severity of the problem - maybe show a brightly lit lightbulb connected to the skin of a motorhome and mother earth. _________________ SHvnDave
SHvnJudy
& Buffy
Living in a 99 Monaco Diplomat |
|
| Back to top |
|
 |
bluegypsy
Joined: 11 Oct 2008
Posts: 2
|
Posted:
Sat Oct 11, 2008 7:00 am Post subject:
|
|
|
| As a workamper who is currently working at a commercial RV park, let me add this: We are now at a top-rated RV park, and I know for a fact that the electrical pedestals are repaired by unqualified, un-certified workampers. As relative newbies, we are learning as we go, and what we've seen here has led us to conclude that we need a circuit protection/testing thingie before our rig gets fried. |
|
| Back to top |
|
 |
lectricman1952
Joined: 11 Oct 2008
Posts: 2
|
Posted:
Sat Oct 11, 2008 7:32 am Post subject:
Re: My Solution |
|
|
| SHvnDave wrote: | Since I first posted here, I have invested in a surge guard to monitor and protect my system (trips at >134V or <92V).
I am also building a box that will be mounted on a grounding rod. The box will plug into a 30A outlet and my 50A plug will plug into the box. The ground rod will be connected to the neutral connection and driven a foot into the earth to ensure I see zero volts on my neutral.
If the ground is not at zero volts, I will connect a separate line at my rig to go directly to earth - this keeps the neutral and the ground several feet apart and should solve most problems.
Note that when you have traveled 8-10 hours and pull into the only campground around, it doesn't matter whether the problem is the campground's because the problem WILL BE yours.
Adrienne - I would really like to see an article in RV Travel so more RVers and park owners become aware of the severity of the problem - maybe show a brightly lit lightbulb connected to the skin of a motorhome and mother earth. |
This is great. Another amateur messing with the park's electrical system.
What you propose is a big violation of the National Electric Code!
And can/may create an unsafe condition for others in the park. |
|
| Back to top |
|
 |
roadramblin
Joined: 19 Feb 2006
Posts: 26
Location: It cha cha cha changes!!!
|
Posted:
Sat Oct 11, 2008 8:22 am Post subject:
Coachlight |
|
|
We have stayed at Coachlight RV Park in Carthage, MO many, many times. As a matter of fact, it is where we are sitting this very minute. Any time we have notified them of anything amiss, they have taken care of it ASAP.
One time I saw a man rinse out his sewer hose by placing it over the water faucet. Eeeewww! I notified the park, and they immediately came to the site and sanitized the faucet.
They could not be better at this park.
We love em! _________________ Barb B |
|
| Back to top |
|
 |
cvrvr
Joined: 27 Nov 2005
Posts: 13
Location: CA, La Crescenta
|
Posted:
Sat Oct 11, 2008 8:51 am Post subject:
|
|
|
That is why, the first thing I do before plugging my shore power cable, is to verify the polarity and voltage of the pedestal receptacle. Also I have a hard wire SurgeGard unit mount in my coach.
Too many campgrounds with bad power problems.
George _________________ George & Karen Wharton
2004 Allegro 30DA W-20
2000 Jimmy toad |
|